Value Processing Behaviors
Animation Value Processing Behaviors
Jump to Animation Keyframe
Common Properties
Animation SharedPointer<Candera::Animation::AnimationPlayer> The animation controlled. AnimationProcessValueBehavior sets the animation to the frame corresponding to the value it receives.
SequenceStartTime FeatStd::Optional<Candera::Animation::SequenceTimeType> The start point of the animation. [ms]
SequenceDurationTime FeatStd::Optional<Candera::Animation::SequenceTimeType> The duration of the animation. [ms]
ControlNode
Candera::AbstractNodePointer Control Node containing a Control Animation.
Diagnostics Value Processing Behaviors
Frame Measurement
Class Reference
Common Properties
RenderTarget Candera::GraphicDeviceUnit* The render target which FPS should be monitored.
Output OutputType::Enum Specifies which information will be output.
DispatchThreshold FeatStd::Optional< FeatStd::Variant > Specifies how much the Output has to change to dispatch an event to its receivers.
Receivers
Effects Value Processing Behaviors
Set Alpha Value
Common Properties
Target Node Candera::AbstractNodePointer The Node which gets the resulting alpha value. If not set, then the node where the behavior is attached to, will be modified.
Set Bitmap Clipping Area
Adjusts the clipping area of a render node. Takes a float value to control the bitmap effect along the X and Y axes. In Relative mode, the value scales the clipping area proportionally (0.0 to 1.0); in Absolute mode, it sets the size in pixel.
AffectXAxis bool Enables or disables scaling in horizontal direction.
AffectYAxis bool Enables or disables scaling in vertical direction.
Mode Mode::Enum Determines how the received value will be interpreted. Options are Absolute and Relative.
ScaleVector Candera::Vector2 This vector is multiplied by the received value and specifies the magnitude by which the clipping area is scaled.
OffsetVector Candera::Vector2 This vector defines the left(X) and top(Y) offset of the clipping area.
Switch Image
Supports
Example Usage
Common Properties
Upload Strategy Enum (OnInit, OnDemand)
Specifies if images are uploaded on demand or when the behavior is instantiated. OnInit may cause an initial delay and keeps all images loaded. OnDemand avoids an initial delay and only keeps one image loaded.
Possible values: OnInit, OnDemand
Target Node RenderNode * The Render Node SwitchImageProcessValueBehavior will switch images on.
Images
SharedPointer<Candera::Image2D>
A list of images which should be available for selection.
Textures
SharedPointer<Candera::TextureImage>
OutOfBoundsHandlingMode
OutOfBoundsHandlingMode::Enum
Behavior when an index greater than the number of images is given.
Possible values: Hold, Clamping
Switch Text
Common Properties
Target Node Candera::AbstractNodePointer The Render Node SwitchTextProcessValueBehavior will switch the text on.
Texts
ArrayProperty<FeatStd::String> Use list of texts (strings) and switch between them.
Zoom Effect
Common Properties
Target Node
Candera::AbstractNodePointer The node whose children are enabled or disabled by ZoomProcessValueBehavior. If not set, then the node where the behavior is attached to will be considered.
Alpha Factors Vector2 Min/Max transparency factors
Zoom Factors Vector2 Min/Max zoom factors
Zoom Distribution Float Distribution of Zoom/Alpha to each side of the selection.
ZoomByLayout bool Whether the zoom is accomplished by layout size.
Transformation Value Processing Behaviors
Resize Group Node
Common Properties
Mode
ScaleVector
Vector2
This vector is multiplied by the received value and specifies the magnitude by which the node is scaled.
Set Node Size
Common Properties
Target Node Candera::AbstractNodePointer The target node which is modified. if not set, then the node where the behavior is attached to, will be modified.
Size Axis AxisType2D::Enum
The axis along which the size is set.
Possible values: AxisX, AxisY
Set Position
Example Usage
Common Properties
Translation Axis 2D
AxisType2D::Enum
The axis along which the position is set.
Translation Axis 3D
AxisType3D::Enum
Possible values: AxisX, AxisY,, AxisZ
Set Rotation
Example Usage
Common Properties
RotationAxis
AxisType3D::Enum
The axis to rotate the node around.
Set Scale
Example Usage
Common Properties
ScaleAlongX bool Enables or disables scaling in horizontal direction.
ScaleAlongY bool Enables or disables scaling in vertical direction.
ScaleAlongZ bool
Enables or disables scaling in Z-direction.
ScaleVector2D Vector2
ScaleVector3D Vector3
Move Node
Example Usage
Common Properties
Target Node Candera::AbstractNodePointer The node TranslateProcessBehavior moves.
Multiplied Vector Vector3 This vector is multiplied by the value TranslateProcessValueBehavior receives and specifies direction and magnitude by which TranslateProcessValueBehavior moves Translated Node. If not set, then the node where the behavior is attached to, will be modified.
AnimationMeter
This behavior is a Behavior Block. It can be dragged&dropped on nodes just like any Behavior. Controls an animation according to the passed value.
Animation Candera::Animation::AnimationPlayer
TThe animation controlled. AnimtionMeter sets the animation to the frame corresponding to a mapped value it receives.
Minimum FeatStd::Variant
Minimum of the Variant value which will be mapped between 0 and 1.
Maximum FeatStd::Variant
Maximum of the Variant value which will be mapped between 0 and 1.
Arithmetic Operation
Common Properties
Operation ArithmeticOperationType::Enum
Arithmetic operation to be performed.
Possible values: Addition, Subtraction, Multiplication, Division, Modulo, Absolute
Operand FeatStd::Variant A number to be used as addend/subtrahend/multiplicant/divisor on provided value.
OutputType VariantValueType::Enum
Type of the Variant forwarded as result.
Possible values: FloatValue, Int32Value, UInt32Value, BoolValue, DoubleValue, Int8Value, Int16Value,  Int64Value, UInt8Value, UInt16Value, UInt64Value, StringValue
Receivers
Clock
Common Properties
SecondsProcessValueBehavior Candera::ProcessValueBehavior*
The behavior that receives the seconds.
MinutesProcessValueBehavior Candera::ProcessValueBehavior*
The behavior that receives the minutes.
HoursProcessValueBehavior Candera::ProcessValueBehavior*
The behavior that receives the hours.
OffsetInMinutes FeatStd::Int32 Offset in minutes to add to time (i.e. for different time zones).
ShowFull24Hours bool If true, hours will be shown from 0-23, otherwise in AM/PM format.
AMText FeatStd::String The string of the AM label.
PMText FeatStd::String The string of the PM label.
AMPMTextBehavior Candera::Behavior*
Sets text 'AM' or 'PM'.
ShowSeconds bool If true, seconds will be shown.
SecondsNode Candera::AbstractNodePointer The node that will be turned off if showing of seconds is disabled.
Dial
Common Properties
CurrentValue FeatStd::Int32 Current value for the dial.
MinimumRotation FeatStd::Float Minimum rotation of the dial.
MaximumRotation FeatStd::Float Maximum rotation of the dial.
StepSize FeatStd::Float Step size in degrees.
KnobNode Candera::AbstractNodePointer Knob node which will be rotated.
Receivers
Filter
Common Properties
Condition Candera::ConditionBehavior* ConditionBehavior for passing the value to the next process value behavior.
Receivers
Forward Value
Note that the target Value - Behavior must have 'Accept Value Event' property enabled.
Example Usage
Common Properties
Event Dispatch Strategy EventDispatchStrategyType::Enum
The way the event gets sent.
Target Node Candera::AbstractNodePointer The target node to which the events are routed. If this property is not set, the event will be routed to the node of the behavior.
Dedicated Behavior
Interpolate Value
If the Animation Mode property is set to Instant, no interpolation will be taking place - the received value will be applied immediately.
Example Usage
Common Properties
Animation Mode InterpolationAnimationMode::Enum
Animation mode sets a specific interpolation type.
Units Per Second Float
Speed at which InterpolateProcessValueBehavior changes its internal value.
This property can only be set when AnimationMode is set to "SpeedBased".
Interpolation Time
UInt32
Time in ms the InterpolateProcessValueBehavior changes its internal value.
This Property can only be set when AnimationMode is set to "TimeBased"
Filter Time Constant Float
The moment before InterpolateProcessValueBehavior’s internal value reaches the received value, the speed at which the former is changing slows down. This prevents a sudden end of movement that can be felt as artificial in some cases.
This property can only be set when AnimationMode is set to either "SpeedBased" or "Timebased".
Receivers
Map Value
Common Properties
InputMin FeatStd::Optional< FeatStd::Variant > [Optional] Smallest value of the interval to check. If Minimum is given as greater than Maximum then the values are internally swapped.
InputMax FeatStd::Optional< FeatStd::Variant > [Optional] Largest value of the interval to check. If Maximum is given as smaller than Minimum then the values are internally swapped.
OutputMin FeatStd::Float Smallest value of the interval mapped to.
OutputMax FeatStd::Float Largest value of the interval mapped to.
Receivers
Map Value Normalized
Common Properties
Reverse bool Toggles the mapping direction. If this property is true, the received value is assumed to be within range from 0.0 to 1.0 and the emitted value is mapped accordingly.
ValueForRange ValueBehaviorBase*
The input value behavior for defining the mapped range.
Receivers
Process Value Changed Event
Example Usage
Common Properties
Sender Candera::AbstractNodePointer The node for which the event shall be emitted. If it is not set then the TargetNode or Node (if TargetNode is not set) will be taken instead.
Minimum Optional<FeatStd::Variant> Minimum threshold of the processed values.
Maximum
Maximum threshold of the processed values.
ConsumeEvent
bool
Receivers
ProcessValueBehavior ArrayProperty
Render a Range
This behavior is a Behavior Block. It can be dragged&dropped on nodes just like any Behavior. Renders a range of nodes according to the passed value.
OperationMode OperationModeType Enum When set to MultipleNodes, EnableNodesProcessValueBehavior will enable the first N children of Group Node. When Operation Mode is set to SingleNode, only Nth node is enabled. N is a number from 0 to number of all children nodes of Group Node. It corresponds linearly to the value EnableNodesProcessValueBehavior receives.
Minimum Optional< FeatStd::Variant > Minimum of the Variant value which gets mapped between 0 and 1.
Maximum
Optional< FeatStd::Variant > Maximum of the Variant value which gets mapped between 0 and 1.
Send ChangeValue on receiving ProcessValue event
Common Properties
ChangeValue ChangeValue::Enum How the event value shall be handled by the receiving behavior
Target Node
This property is only visible if EventDispatchStrategy is set to "Direct", "Broadcast", "Bubble" or "Tunnel".
This property only visible if EventDispatchStrategy is set to "DedicatedBehavior".
Receivers
Set Selected State
Smooth Value
Class Reference
Common Properties
SmoothingFactor FeatStd::Float The factor how fast the output value should adapt to the input value. Valid values are between 0.0 and 1.0
Receivers
Render Child Nodes
Common Properties
Levels FeatStd::UInt8 Number of levels to step down through groups. Default is zero.
Format String
Example Usage
Common Properties
Text String Text that TextBehavior will change the Node to. Supports formatting for one variable that corresponds to the value TextProcessValueBehavior2D receivers.
Style SharedPointer <Candera::TextRendering::SharedStyle> The style that will be set to the Text Node.
Alignment TextNode2DLayouter::TextAlignment
Possible values: Auto, Left, Center, Right
Multiline bool If multi line is disabled, then the new line control characters will be ignored and text will always be rendered in one line.
Line Spacing PixelSize (UInt16) Defines the distance between the baselines of successive lines of type.
Word Wrap Bool If word wrapping is enabled then the lines that exceed the client area will be split during arrangement into multiple lines.
Trimming TextNode2DLayouter::Trimming
Possible values: None, Ellipsis, CustomText
TrimmingText FeatStd::String
This property is only visible if Trimming is set to "CustomText".
Track Angle on Drag
Common Properties
TouchNode Candera::AbstractNodePointer A node that is used to collect information about the touch.
Receivers
Drag on Track to Value
Common Properties
UseCenter bool If true, the center value defined for the knob bitmap is used to align the knob to the value position, otherwise the calculated center.
TrackDirection TrackDirection::Enum
Defines if the position will be tracked horizontally or vertically
LeftTouchMargin FeatStd::Float Defines the size for extending or shrinking the touch-sensitive area at the left border of the knob. The size is given in percentage of the knob width. Positive values extend, negative values shrink the area.
RightTouchMargin FeatStd::Float Defines the size for extending or shrinking the touch-sensitive area at the right border of the knob. The size is given in percentage of the knob width. Positive values extend, negative values shrink the area.
TopTouchMargin FeatStd::Float Defines the size for extending or shrinking the touch-sensitive area at the top border of the knob. The size is given in percentage of the knob height. Positive values extend, negative values shrink the area.
BottomTouchMargin FeatStd::Float Defines the size for extending or shrinking the touch-sensitive area at the bottom border of the knob. The size is given in percentage of the knob height. Positive values extend, negative values shrink the area.
OnKnobDragOnly bool The position will only be updated when the Knob gets dragged, otherwise clicking on the control will move the knob to the position.
UseExcclusiveMode
bool
Enabling the option prevents some controls (e.g. Slider) from loosing the touch when leaving the node area.
DraggedNode
Defines the node to move along the track, to determine the hit area and to determine the position change relative to its center.
Receivers
Action on Value
Example Usage
Common Properties
Condition ConditionBehavior* The ConditionBehavior that TriggerBehavior passes a value to and expect a response from to see if Action needs to be invoked.
Actions ActionBehaviorArrayProperty The set of ActionBehaviors that TriggerBehavior invokes in the event that it receives a positive response form Condition.
Consume Event bool Set this flag to false if the event should not be consumed by the trigger. By default it is set to true and if the trigger evaluates to true the event will not be routed to any other behavior.
Value
Example Usage
Common Properties
Minimum FeatStd::Optional< FeatStd::Variant >
Minimum of the Variant value. If Minimum is given as greater than Maximum then the values are internally swapped.
Maximum FeatStd::Optional< FeatStd::Variant > Maximum of the Variant value. If Maximum is given as smaller than Minimum then the values are internally swapped.
IntervalHandling IntervalHandling::Enum
Select how the behavior should react when the minimum or maximum limit is exceeded.
Possible values: Limit, Cycle, Ignore
AcceptValueEvent bool Set this flag to true to make the value changeable by events/actions.
BroadcastProcessValueEvent bool Set this flag to true to broadcast ProcessValue event even if value did not change.
DispatchStrategy
By default the event that indicates that this value behavior has been changed (ValueChangedEvent) is dispatched only on the node to which the value behavior is attached (CgiStudioControl::EventDispatchStrategyType::Direct). To change this you have to select a different dispatch strategy.
DedicatedBehavior
Candera::Behavior*
The dedicated behavior that will receive ValueChangedEvent when DedicatedBehavior dispatch strategy is selected.
This property is only visible if DispatchStrategy is set to "DedicatedBehavior".
TargetNode
The node on which the for which the EventDispatchStrategy will be applied. If it is not set then the Node will be taken instead.
This property is only visible if DispatchStrategy is set to "Direct", "Broadcast", "Bubble" or "Tunnel".
Variant
Candera::Variant Specifies the type and the value to pass onto Process Value Behavior.
Receivers
Value Generator
The Value Generator is a demo behavior. It allows you to configure minimum and maximum values, period, and update interval, and is used for UI verification and simulation purposes. It appears in the tool when CONTROLS_DEMO_BEHAVIORS_ENABLED is enabled via CMake.
Common Properties
GeneratorFunction Enum The type of function used to generate values (linear, sin, etc.)
Minimum Float The minimum for the generated values.
Maximum Float The maximum for the generated values.
OffsetMs Int The time offset where the function is evaluated.
PeriodMs Int The time period after which the generated values repeat.
SamplerateMs Int The update rate of the generated value.
GenerateValues bool
Set this flag to true to generates values at sample rate. If set to false, no values are generated.
Dedicated Behavior Candera::ProcessValueBehavior*
The dedicated process value behavior that will receive the change value event. This property can be set in the right side of the Scene Tree panel.